I am a bit confused by conductor derating within conduit. A snipit of the table is:
4-6 current-carrying wires, derate 80%
7-9 current-carrying wires, derate 70%
10-20 current-carrying wires, derate 50%
These numbers are irrelevent to the size of the conduit. 10 wires derate at 50% in 3/4" EMT and also in 2" EMT and 4" EMT. However, putting 2 sets of 5 wires in two 1/2" EMT runs, and we're up to 80% derating.
Ok, I understand that 10 wires in 3/4" EMT would need to be derated (due to heat), but there's more air in the 2" conduit, so why doesn't the 2" EMT have a higher derating at 10 wires than 3/4"?? Am I missing something??
The reason I'm asking is this:
I want to run two 220V 20A circuits and two 110V 20A circuits from my subpanel using 12 AWG copper. That's 8 current-carrying wires plus a shared ground, which is 9 12AWG wires total. 3/4" EMT can handle 16 12AWG wires, so no problem there. However, that would derate to 70%, which is 17.5 Amps, insufficient for the 20Amp requirements.
So it looks like I need to use two runs of 1/2" EMT OR 10AWG wire ($$$$).
Am I missing something??
4-6 current-carrying wires, derate 80%
7-9 current-carrying wires, derate 70%
10-20 current-carrying wires, derate 50%
These numbers are irrelevent to the size of the conduit. 10 wires derate at 50% in 3/4" EMT and also in 2" EMT and 4" EMT. However, putting 2 sets of 5 wires in two 1/2" EMT runs, and we're up to 80% derating.
Ok, I understand that 10 wires in 3/4" EMT would need to be derated (due to heat), but there's more air in the 2" conduit, so why doesn't the 2" EMT have a higher derating at 10 wires than 3/4"?? Am I missing something??
The reason I'm asking is this:
I want to run two 220V 20A circuits and two 110V 20A circuits from my subpanel using 12 AWG copper. That's 8 current-carrying wires plus a shared ground, which is 9 12AWG wires total. 3/4" EMT can handle 16 12AWG wires, so no problem there. However, that would derate to 70%, which is 17.5 Amps, insufficient for the 20Amp requirements.
Am I missing something??