Bottom line, no "code" requirement for a maximum.
The thing to keep in mind is added resistence. But if you have more than 10 outlets on one circuit, you might want to reexamine your plan....
I have 16 x 20amp outlets, 8 per circuit. Also ran one 15amp circuit for lights and small things.
BTW, if you can, make sure the first outlet on the run is a GFCI, or use a GFCI circuit breaker.
We won't go into how my extention cord fell into the bucket of water, but I'm a big fan of GFCI.....
Jim
What is the maximum number of 15 or 20A, 125V receptacle outlets permitted on a 20A, 120V general-purpose branch circuit in a commercial occupancy?
A1 For commercial occupancies, the NEC requires each receptacle outlet to be calculated at 180 VA [220.14(I)]. Therefore, the maximum number on a 20A circuit would be 13.
Circuit VA = Volts x Amperes
Circuit VA = 120V x 20A
Circuit VA = 2,400 VA
Number of Receptacles = 2,400 VA/180 VA
Number of Receptacles = 13
Note: According to the NEC Handbook, published by the NFPA, general-purpose receptacles aren't considered a continuous load.
Q2 What is the maximum number of 15 or 20A, 125V receptacle and lighting outlets permitted on a 15A, 120V general-purpose branch circuit in a dwelling unit?
A2 The NEC doesn't limit the number of receptacle and lighting outlets on a general-purpose branch circuit in a dwelling unit. See the NFPA's NEC Handbook for more information.
Although there's no limit on the number of lighting and/or receptacle outlets on dwelling general-purpose branch circuits, the NEC does require a minimum number of circuits to be installed for general-purpose receptacles and lighting outlets [210.11(A)]. In addition, the receptacle and lighting loads must be evenly distributed among the required circuits [210.11(B)].
Caution: Not likely, but there might be a local electrical requirement that limits the number of receptacles and lighting outlets on a general-purpose branch circuit.