220 Volt Connection ?

Status
Not open for further replies.

David Turner

David
Corporate Member
I would like to run my new 220 Volt table saw off of my dryer receptacle ( I did it that way in Michigan). What's up with this 4 stab receptacle? My extension cord from up North has a typical 3 stab male plug. Does NC require 2 grounds?

David Turner
North Raleigh
 

Phil S

Phil Soper
Staff member
Corporate Member
My understanding is many new dryers have 120 volt controls which means a current carrying neutral is required plus a safety ground. You could hook your table saw to the two hots plus the ground
 

Rwe2156

DrBob
Senior User
It is so easy to add a 20A 240V breaker and the correct wire, so why not just do it right?
 

junquecol

Bruce
Senior User
All dryers use 120 v controls and motor. No longer is the ground allowed to be used as neutral. Been this way in mobile homes for MANY years. When I built my last house (1992) if you use SE cable, then ground could serve as neutral also, but if you used Romex, then they had to be two separate wires.
 

FlyingRon

Moderator
Ron
Actually, it was the other way around. The neutral used to be allowed to be the equipment ground on dryer and range circuits.

Your 220V tool doesn't need a neutral, as pointed out.
 